Closed
bsimmons-onboard
started this conversation in
General
Replies: 1 comment 1 reply
|
If I am following the manual correctly, the 4 quadrant power factor register appears to be a converted version of the power factor reading to provide context on the PF quadrant that the power readings are in. It looks like the meter also provides the reading of the non-converted power factor value between -1 and 1. I am questioning the necessity of bringing the register field in as the user can determine the quadrant using the kW and kVAR readings. Is there a specific use case you would see addition of the register field helping? |
1 reply
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
Uh oh!
There was an error while loading. Please reload this page.
Hello, we would like to model a Schneider Electric power meter (PM5000 series) that measures 4 quadrant power factor. These values can vary between [-2, 2], but the current standard for power factor unit is limited to [-1,1].
Is it desirable to extend the allowable power factor range, or create new telemetry fields and a units for 4 quadrant power factors?
This is detailed in pages (190-192) https://www.se.com/us/en/download/document/HRB1684301/